So there I am doing IR tests on an existing lighting circuit prior to moving it from a BS3036 CU to a new RCBO CU. All lamps, tubes, dimmers etc. removed, checked for caps in the fluorescent fittings etc. All light switches on.
L-E checks OK, N-Es check OK, L-N - Zero Ohms! WTF? Did a continuity check - L-N 140 Ohms!
Turn off all light switches - no change. Re-connect to the old CU and check every light works OK. Measure current with all lights off - about 10mA. Hmm, 230/140 is a lot more than 10mA!
Disconnect, test again - no change. Rack my brains and realise the under cabinet tube in the kitchen is still connected - but switched off. Disconnect that and test again. No change. Made a cup of tea.
An then it came to me - DOH! The shaver socket in the bathroom is connected to the lighting circuit and the 140 Ohms is the DC resistance of the transformer primary. Disconnect and all is well.
Moral of this story is ---- A nice cup of tea makes everything OK