Hi All,
I am after some advice on the structural calculation I have for first floor beam support which replaces internal brick wall.
The calculations have been done a while ago and I can’t get in touch with the architect and the structural engineer who did it.
At the time it was done I didn’t look in the details, but now when it came to build it I noticed that the load assumptions are not correct for few reasons:
1) The beam supports floor joist to both sides of the house and the total floor space is around 18m2
2) As the project started it has been decided to make the beam slightly longer – 3.45m span
3) Due to above it now also picks up 8x3 joist (0.3m from the post) which supports block partition wall on the first floor.
With some assumptions I found online the load may look like:
1)Floor load (0.5kN * 1.4 + 1.5kN * 1.6 = 3.15kN/m2 – first floor factored dead+ factored live load)
3.15kN *18 / 2 = 28.35kN
2) Bathroom wall straight above the beam – 2.50kN x 3m x 2.2m = 16.5kN * 1.4 = 23.1kN
3)1st floor partition wall 2.5kN x 2.5m x 2.2m / 2 =6.8kN * 1.4 = 9.6kN
Total load – 61kN, or per meter of the beam – 18kN/m
I am not adding 1st floor celling load as celling joist are connected to the loft floor joist (loft conversion).
Without understanding full details of the below calculations I can see that provisioned 152UC37 and supporting 90x90x5 SHS post are well over dimensioned?
Like
Fv = 128.3 > 11
Mcx = 110 > 8
Mb = 77 > 8
Am I right assuming that extra load which the beam/post going to get well within the safe limits?
Any advice/comments much appreciated!
I am after some advice on the structural calculation I have for first floor beam support which replaces internal brick wall.
The calculations have been done a while ago and I can’t get in touch with the architect and the structural engineer who did it.
At the time it was done I didn’t look in the details, but now when it came to build it I noticed that the load assumptions are not correct for few reasons:
1) The beam supports floor joist to both sides of the house and the total floor space is around 18m2
2) As the project started it has been decided to make the beam slightly longer – 3.45m span
3) Due to above it now also picks up 8x3 joist (0.3m from the post) which supports block partition wall on the first floor.
With some assumptions I found online the load may look like:
1)Floor load (0.5kN * 1.4 + 1.5kN * 1.6 = 3.15kN/m2 – first floor factored dead+ factored live load)
3.15kN *18 / 2 = 28.35kN
2) Bathroom wall straight above the beam – 2.50kN x 3m x 2.2m = 16.5kN * 1.4 = 23.1kN
3)1st floor partition wall 2.5kN x 2.5m x 2.2m / 2 =6.8kN * 1.4 = 9.6kN
Total load – 61kN, or per meter of the beam – 18kN/m
I am not adding 1st floor celling load as celling joist are connected to the loft floor joist (loft conversion).
Without understanding full details of the below calculations I can see that provisioned 152UC37 and supporting 90x90x5 SHS post are well over dimensioned?
Like
Fv = 128.3 > 11
Mcx = 110 > 8
Mb = 77 > 8
Am I right assuming that extra load which the beam/post going to get well within the safe limits?
Any advice/comments much appreciated!