No, not all boiler trips generate a fault code which would then normally require a boiler reset, it should though have generated a status code.
For interest, some numbers below from someone who had a WB Greenstar 36kw CDI combi and the burner was tripping at d.040 (equivalent) of ~ 75C with a DHW flow of 9.2LPM at 44.5C (setpoint 55C), and a boiler output of only 16.37kw.
A new PHEX was installed and the numbers then showed d.040 (equivalent) of only 64.5C with a DHW flow of 9.9 LPM at 54.5C (setpoint 55C), but the boiler output was then 24.1kw.
Just to update while I'm waiting for the Mrs to decide to shower/bath:
The boiler was installed 2 years to the day, pretty much. The system was power flushed as part of the installation. It was serviced after about 16 months.
I think I can safely say that this "hot water going tepid for a short period" e.g. 10 secs, has been happening from the start, although it happens so infrequently that it's difficult to say how often and what the contributing factors might be. Apart from this minor issue, I've been very pleased with the boiler, especially the power of the shower - it's miles better than the trickle (exaggeration) that we used to get from our gravity system. It works perfectly for the majority of the time.