Well, there hasn't been a post about this thorny subject for a day or two, so here's mine...
Having looked at all the relevant guides, I still find the subject confusing. I have fitted an electric shower (with 45A DP isolator & pullcord), new zone 3 ceiling light and SELV fan (transformer and isolator in cupboard beyond zone 2) to a bathroom containing a metal (enamelled) bath with copper pipes, a sink with copper pipes and a radiator with copper pipes. There's also a copper gas pipe running through alongside the radiator pipes.
The existing bonding runs from the bath hot & cold (under the bath) to the radiator flow & return and on to the earth of a socket in the next room (the wiring of which is made from under the bath).
Any ideas what I need to do to bring this installation in line with current regs? I have read that all exposed metal parts (shower hose?) must be connected to all extraneous metal parts (radiator, bath, taps?), but this could easily become impractical. I don't understand why , under phase-earth fault conditions, the CPC of, say, the shower, would not be an adequate path for the fault current and trip the MCB (RCD).
I understand that, in a bathroom, you don't want extraneous metallic parts like a radiator and taps being at a different potential, but why would they be anyway? If one became live because of a fault and the other not, then a potentially fatal PD would esist between them, but...hmmm...this is where I get confused!
I understand that copper pipes may not be continuous back to the earthed water main due to plastic pipe additions, but, na, still confused! Is there a really user-friendly guide to all this anywhere??
Having looked at all the relevant guides, I still find the subject confusing. I have fitted an electric shower (with 45A DP isolator & pullcord), new zone 3 ceiling light and SELV fan (transformer and isolator in cupboard beyond zone 2) to a bathroom containing a metal (enamelled) bath with copper pipes, a sink with copper pipes and a radiator with copper pipes. There's also a copper gas pipe running through alongside the radiator pipes.
The existing bonding runs from the bath hot & cold (under the bath) to the radiator flow & return and on to the earth of a socket in the next room (the wiring of which is made from under the bath).
Any ideas what I need to do to bring this installation in line with current regs? I have read that all exposed metal parts (shower hose?) must be connected to all extraneous metal parts (radiator, bath, taps?), but this could easily become impractical. I don't understand why , under phase-earth fault conditions, the CPC of, say, the shower, would not be an adequate path for the fault current and trip the MCB (RCD).
I understand that, in a bathroom, you don't want extraneous metallic parts like a radiator and taps being at a different potential, but why would they be anyway? If one became live because of a fault and the other not, then a potentially fatal PD would esist between them, but...hmmm...this is where I get confused!
I understand that copper pipes may not be continuous back to the earthed water main due to plastic pipe additions, but, na, still confused! Is there a really user-friendly guide to all this anywhere??