This is true, that at least a 100mA upfront RCD is retained, Although there is some instances where it can be excluded, but all circuits at the board must then be covered by at 30mA RCD protection.Hi, you may have to retain the 100ma 'upfront' and add a 30ma on your socket circuit. Your electrian will advise if the TT earth is adaquate.
The ideal situation would be to have all circuits protected individually by RCBOs, but to comply to the regs, in your situation you need to protect newly buried cable and newly installed sockets by 30mA RCD.Thanks for the info DS. Sorry to ask, but would I need a separate RCD for each of the upstais and downstairs socket circuits or can it be wired to cover both circuits with a common RCD?
RCBOs are RCDs.
The ideal situation would be to have all circuits protected individually by RCBOs, but to comply to the regs, in your situation you need to protect newly buried cable and newly installed sockets by 30mA RCD.
As you have a TT earthing arrangement, you have to cover the whole installation by RCD. Which I understand exists in the form of a 100mA RCD.Would I need to fit a RCD to cover the annexe?
However, is it possible to fit RCBOs in my situation as you suggest without changing the CU? I need to look at costings. Alternatively, any suggestions, given the 3 socket circuits I have for additional 30mA RCDs?
As would be any newly buried cable, that does not meet the existing requirement. But I also recall addition of socket outlet.You can still buy rbo's for the board. You have not actually added any circuits ? You have moved a socket and replaced a damaged one. If you add a circuit or a socket the addition should have RCD protection.
DS
As would be any newly buried cable, that does not meet the existing requirement. But I also recall addition of socket outlet.
You can still buy rbo's for the board. You have not actually added any circuits ? You have moved a socket and replaced a damaged one. If you add a circuit or a socket the addition should have RCD protection.
As would be any newly buried cable, that does not meet the existing requirement.