Hi
My last post was to simply clarify that that I did not add a circuit as there seemed to be some doubt and also to state that the routing of the cables was correct
As mentioned earlier:
I am getting an electrician as I want to fit the 30mA RCDs for the circuits as suggested to me (as my current one is 100mA anyway) or even fit RCBOs if possible. That was the reason for evaluating the propsective RCBO costs. My post confirms this:
Perhaps there was some misunderstanding here.
Thanks
My last post was to simply clarify that that I did not add a circuit as there seemed to be some doubt and also to state that the routing of the cables was correct
As mentioned earlier:
The ideal situation would be to have all circuits protected individually by RCBOs, but to comply to the regs, in your situation you need to protect newly buried cable and newly installed sockets by 30mA RCD.
As you already have an upfront RCD, it would be difficult/impossible to prevent complete loss of power if that device trips.
But it would be expected that a 30mA device would discriminate over a 100mA device.
It would be best to protect sockets circuits individually with 30mA, but BS7671 (wiring regs) could allow for them both to be on the same 30mA RCD, providing lighting circuits are not.
I am getting an electrician as I want to fit the 30mA RCDs for the circuits as suggested to me (as my current one is 100mA anyway) or even fit RCBOs if possible. That was the reason for evaluating the propsective RCBO costs. My post confirms this:
However, is it possible to fit RCBOs in my situation as you suggest without changing the CU? I need to look at costings. Alternatively, any suggestions, given the 3 socket circuits I have for additional 30mA RCDs?
Perhaps there was some misunderstanding here.
Thanks