hello there im going to buy SWA but the company only sell XLPE not PVC SWA would this be fine for my instalation
XPLE is rated at 90ºC whereas PVC is rated at 70ºC.
To use XPLE at it's full current carrying capacity you need to ensure the terminations are also rated at 90ºC, otherwise use the PVC rated values for that size of SWA and use it as a 70ºC cable.
Another thing to note is that the CSA of the steel armour in XPLE differs slightly to that in PVC, see the info in the wiki here: //www.diynot.com/wiki/electrics:swa-earthing
Bah, beaten to it
hello there im going to buy SWA but the company only sell XLPE not PVC SWA would this be fine for my instalation
Could you translate that into a language which people here can understand?ok but if you are operating the xlpe at 70deg then i think the minimum csa of the swa is the same as the 70deg swa so it would comply? ie: 25mm swa minimum csa = 36.1 csa swa 2 core xlpe =42