Swapped radiator now boiler won’t fire up

Joined
19 Apr 2016
Messages
9
Reaction score
1
Country
United Kingdom
Swapped bathroom radiator, bled radiators and topped up pressure to 1.5 but my Worcester greenstar 28i junior won’t fire up (it was absolutely fine before this).
It’s flashing blue light (mainly off) and reset flashing too.
It sounds like it is making attempts to fire up but after a few attempts times out and asked to be reset again.
I cannot think of any reason why swapping a rad would cause this so any help much appreciated.
Many thanks
 
Sponsored Links
No more this
 

Attachments

  • image.jpg
    image.jpg
    249.8 KB · Views: 67
Sponsored Links
Just an update on this:

I reset again this morning now I have hot water so at least we can finally have a shower

Downside is the central heating still won’t come on
 
Is it attempting to come on?, if so, immediately after using hot water c/o to CH and see if the pressure gauge on the boiler front is fluctuating or stays steady.
 
Is it attempting to come on?, if so, immediately after using hot water c/o to CH and see if the pressure gauge on the boiler front is fluctuating or stays steady.
Unfortunately it isn’t attempting to come on.
 
At the top of the heat exchaanger there is a plastic bayonet fitting with a clear hose coming off, turn the bayonet until water comes out of the tube, be carefull the water may be extremely hot
 
At the top of the heat exchaanger there is a plastic bayonet fitting with a clear hose coming off, turn the bayonet until water comes out of the tube, be carefull the water may be extremely hot
Ah if I knew you I would owe you a drink sir.
It’s sorted now many thanks
 
At the top of the heat exchaanger there is a plastic bayonet fitting with a clear hose coming off, turn the bayonet until water comes out of the tube, be carefull the water may be extremely hot
Is that unique to Worcester boilers?, I think most boilers do have AAVs, but inside the boiler casing and are generally shut off after venting tp prevent leakage.
 
Is that unique to Worcester boilers?, I think most boilers do have AAVs, but inside the boiler casing and are generally shut off after venting tp prevent leakage.
unique to the Ri range of WB although i seem to remeber an ariston with similar
 