I have found another calculator It has come up with 5.83 KW required, ignoring DHW charging.
Which is about the same as your rads.
I forgot to mention that the boiler charges a hot water cylinder (Megaflow). Would it take longer to charge, if the boiler max output is dropped?
No. Megaflow say allow 3kW for heating the cylinder so, if you have 6kW for heating, you should set the boiler to 9kW. This allows both CH and HW to run at the same time.
Also, I have a VRC430 weather compensator. Would this avoid the need to drop the max output?
Not really.
How has this been installed - in the boiler or mounted on the wall?
Has the correct heating curve been selected?
Has the external sensor been fitted in the correct place? i.e.
* on a N or NW facing wall
* no draughty location
* no direct sunlight
* no influence from heat sources
If you want to adjust the output the instructions are in the installation manual page 34. And if you don't have this, here they are:
Adjusting the central heating output (range rating)
• Press the “i” and “+” buttons simultaneously.
• Keep the “+” button pressed until “d.0” is displayed.
(Note: The display runs from “d.0” to “d.99” before restarting at “d.0”.)
• Press the “i” button. The “=” symbol is displayed. The part load setting is now displayed in kW.
• Use the “+” and “–” buttons to increase or decrease the value in steps of 1 kW. The displayed value will flash while the adjustment procedure is being carried out.
• Push the “i” button for about five seconds, or until the display stops flashing. The value is now saved to memory.
The display will now return to its normal state (current heating system flow temperature, e.g. 45 °C).
• Press the “i” and “+” buttons simultaneously to cancel adjustment mode.
Adjustment mode is also cancelled if no button is operated for a period of 4 minutes.
I mean 1/8 to 1/4 of a turn open.
That sounds about right. The effective working range of the typical LS valve is from closed to 1 or 1 1/2 turns open.