I was replacing a electric hand water heater today. This has the following isolation switch, which is powered by a 32 Amp Breaker.
I switched the above on and off and verified power at the heater using my two pole tester. Once I was satisfied that this was the correct isolation point, I switched it off.
Before I could start working on replacing the heater, I noticed that the light on this switch was intermittently lighting up whilst the switch was in the off position. Here's a picture of it:
When this was the case, there was power at the heater - despite the switch being in the off position. Given that I spotted this, I switched off the breaker before doing the work.
I did then open up the switch and all the supply and load cables look good as do the lights for the indicator.
Q. Can you please shed some light on what may be causing this?
Also, would it have been reasonable to start working on replacing the heater after isolating it at this switch (after testing with the 2 Pole tester) or is this bad practice?
I switched the above on and off and verified power at the heater using my two pole tester. Once I was satisfied that this was the correct isolation point, I switched it off.
Before I could start working on replacing the heater, I noticed that the light on this switch was intermittently lighting up whilst the switch was in the off position. Here's a picture of it:
When this was the case, there was power at the heater - despite the switch being in the off position. Given that I spotted this, I switched off the breaker before doing the work.
I did then open up the switch and all the supply and load cables look good as do the lights for the indicator.
Q. Can you please shed some light on what may be causing this?
Also, would it have been reasonable to start working on replacing the heater after isolating it at this switch (after testing with the 2 Pole tester) or is this bad practice?