Hi,
I have a new installation of an Air Source Heat Pump (Grant UK Aerona), and a horizontal Tempest 200l pressurised cylinder. It has a single immersion heater, which is controlled by a Timeguard FST77 7 Day Fused Spur Timeswitch, and the whole system is controlled by a ESI ESCTD Mechanical Dual Cylinder Thermostat (set to the maximum of 65 degrees currently)
I've also added a MyEnergi Eddi with PT1000 probes for monitoring the temperature in the top and bottom of the cylinder using the dry pockets.
My installer has set the immersion heater to come on once a week for an hour using the Timeguard timer. This is to ensure that the water temperature goes above 60 degrees to kill legionella bacteria, as I understand the ASHP is not capable of getting it to this temperature on it's own.
BUT, I'm not convinced it's working. My PT1000 temperature probes are showing that the temperature never goes above 51 degrees, and I can see that the immersion heater stops drawing power even when the green light is on the timeswitch, and I've set it to boost.
To verify this, I've also used a manual temperature probe in the cylinder pocket. I managed to get a readout of 53 degrees by pushing it hard against the pocket walls. I got a readout of 55 degrees from the hot water coming out of the bathroom tap (from an un-insulated run of about 5 metres). It's still a long way off the 65 degrees set on the cylinder thermostat though.
So my questions are:
1. Is my temperature monitoring reliable? Is there something better I can do to verify the temperature in the tank? Perhaps something to measure the temperature of the water flowing directly out the top of the tank? Is there an inline temperature monitor that I can install on the 22mm pipe that is more accurate than the dry pockets?
2. What would be stopping the temperature getting above 50-55 degrees? Does the immersion have a cutout?
As a separate question - is it OK, that I have 22mm pipe coming out of the cylinder for about 3 metres before it reduces to 15mm? 22mm pipe holds about 3 times the amount of water as 15mm, so I think this will increase the amount of cold-run-off, and the amount of hot water that I'll be wasting in the pipes. What's standard here?
I have a new installation of an Air Source Heat Pump (Grant UK Aerona), and a horizontal Tempest 200l pressurised cylinder. It has a single immersion heater, which is controlled by a Timeguard FST77 7 Day Fused Spur Timeswitch, and the whole system is controlled by a ESI ESCTD Mechanical Dual Cylinder Thermostat (set to the maximum of 65 degrees currently)
I've also added a MyEnergi Eddi with PT1000 probes for monitoring the temperature in the top and bottom of the cylinder using the dry pockets.
My installer has set the immersion heater to come on once a week for an hour using the Timeguard timer. This is to ensure that the water temperature goes above 60 degrees to kill legionella bacteria, as I understand the ASHP is not capable of getting it to this temperature on it's own.
BUT, I'm not convinced it's working. My PT1000 temperature probes are showing that the temperature never goes above 51 degrees, and I can see that the immersion heater stops drawing power even when the green light is on the timeswitch, and I've set it to boost.
To verify this, I've also used a manual temperature probe in the cylinder pocket. I managed to get a readout of 53 degrees by pushing it hard against the pocket walls. I got a readout of 55 degrees from the hot water coming out of the bathroom tap (from an un-insulated run of about 5 metres). It's still a long way off the 65 degrees set on the cylinder thermostat though.
So my questions are:
1. Is my temperature monitoring reliable? Is there something better I can do to verify the temperature in the tank? Perhaps something to measure the temperature of the water flowing directly out the top of the tank? Is there an inline temperature monitor that I can install on the 22mm pipe that is more accurate than the dry pockets?
2. What would be stopping the temperature getting above 50-55 degrees? Does the immersion have a cutout?
As a separate question - is it OK, that I have 22mm pipe coming out of the cylinder for about 3 metres before it reduces to 15mm? 22mm pipe holds about 3 times the amount of water as 15mm, so I think this will increase the amount of cold-run-off, and the amount of hot water that I'll be wasting in the pipes. What's standard here?