1. Ring: I have cross connected phase and neutral at the CU and measured resistance at each socket to confirm no bridges - readings should not vary more than 0.05 ohms as I understand. Should I be concerned that using the plug attachment for the megger on the front of the socket the readings are high AND they vary (e.g. 0.5ohms - 1.5 ohms) when they are 0.3 when the face is dropped? They seem the vary with swtiching the socket on and off, and is the same for all of the sockets ... BUT is this what is often seen????
2. Ring: To Calculate R1+R2 is it acceptable to measure r1 and r2 and then calculate or should you always cross connect phase and cpc and go to each socket to take the highest reading?
2. Ring: To Calculate R1+R2 is it acceptable to measure r1 and r2 and then calculate or should you always cross connect phase and cpc and go to each socket to take the highest reading?