I realise this question have been asked before but I still have found no definitive answer.
Unusually this is a New house build.
Kitchen ring final circuit using 20 amp dp switches to isolate the white goods (including F/freezer etc and d socket) on a 32amp CB.
All wiring 2.5mm.
Appliance: Oven (mircrowave combi) 3.65kW 16amp.
Qu. It is within regs to have it connected unfused to the dp switch on the radial 2.5mm cable.
Further information.
This is one of two ovens placed vertically with the lower oven (identical load of 3.65kw) on a separate 6mm radial.
Also with a induction hob (5.2kW) with a separate 6mm radial.
I don’t think it is, and have been in conversation with the electrician who won’t provide a cct diagram, but I have a photo of the installation to B boxes.
He reassures me that the cabling is ‘adequate’ and the 32amp MCB is okay.
But surely, unlike say a F Freezer which protected by its fuse, this oven is not and in theory the 2.5mm radial could be overloaded, although unlikely unless the load changes.
Is there any specific reg. this is in violation of, that I could quote, or is it just poor practice, bending the regs?
Unusually this is a New house build.
Kitchen ring final circuit using 20 amp dp switches to isolate the white goods (including F/freezer etc and d socket) on a 32amp CB.
All wiring 2.5mm.
Appliance: Oven (mircrowave combi) 3.65kW 16amp.
Qu. It is within regs to have it connected unfused to the dp switch on the radial 2.5mm cable.
Further information.
This is one of two ovens placed vertically with the lower oven (identical load of 3.65kw) on a separate 6mm radial.
Also with a induction hob (5.2kW) with a separate 6mm radial.
I don’t think it is, and have been in conversation with the electrician who won’t provide a cct diagram, but I have a photo of the installation to B boxes.
He reassures me that the cabling is ‘adequate’ and the 32amp MCB is okay.
But surely, unlike say a F Freezer which protected by its fuse, this oven is not and in theory the 2.5mm radial could be overloaded, although unlikely unless the load changes.
Is there any specific reg. this is in violation of, that I could quote, or is it just poor practice, bending the regs?