I was asked to look at the electrical installation of a heating system that packed up. No hot water or heating.
The system is comprised of a gas boiler, a thermal store cylinder (I hadn't seen this set up before), a pump, a 2 channel programmer, a room thermostat, a cylinder thermostat and a 3-port diverter valve with a spring return.
Ist thing I noticed was the programmer has a supply but no output to either channel, I replaced the programmer with the same model and it fired up. I started to look at the operation. The 3-port diverter valve is normally allowing water from the boiler into the HW cylinder, when the cylinder stat is satisfied the 3-port valve gets a supply and opens up the heating port (A) and shuts off the HW port (B). However, the cylinder thermostat was permanently closed so the heating didn't come on. I thought it a bit odd that the timer and the cylinder stat were both no good.
I replaced the cylinder stat, its a type that goes into a pocket on the side of the cylinder. Its a Honeywell Aquastat with no external controls and a temperature range of 70 - 140 C with a dial inside the cover (no over temperature cut-out). I fitted that and left it at the lowest setting as per the previous unit. It fired up, got to temperature and went off I turned up the room stat and the valve opened and the heating came on. It all seemed fine, so off I went.
Got a call the next morning saying that the everything was OK except the shower ran out of hot water after about a minute. It has previously worked fine before the breakdown. I thought I would turn up the cylinder stat a bit, so I did and the pump start sending the boiler water into the cylinder but it didn't last long and turned off. I thought it couldn't have increased the water temperature that quick? As an experiment I turned it up a bit more but the same again. Anyway I left it overnight, the occupant said it was not much better the next day. As an experiment I cut out some of the insulation on the cylinder (it the foam covered type) and fitted a strap on cylinder stat and this seemed to operate as you would expect. So now I am wondering if the probe type stat I fitted is not calibrated correctly, but that seems a bit of a coincidence. I have read that this type of stat is not considered suitable but I thought it would be ok for one night. I set it at 60 degrees C. They phoned the following day to say it was better but still didn't last long enough in the shower. I'm not sure why the surface cylinder stat is not considered suitable but I was thinking of setting it at 70 degrees C for tonight to check for an improvement?
Any thoughts would be much appreciated. I wasn't sure how or why the probe stat wasn't working properly but I suppose it could be just faulty, but it seems odd that the programmer went kaput, and the last cylinder stat and now this one seems to switch off early?
I was asked to look at the electrical installation of a heating system that packed up. No hot water or heating.
The system is comprised of a gas boiler, a thermal store cylinder (I hadn't seen this set up before), a pump, a 2 channel programmer, a room thermostat, a cylinder thermostat and a 3-port diverter valve with a spring return.
Ist thing I noticed was the programmer has a supply but no output to either channel, I replaced the programmer with the same model and it fired up. I started to look at the operation. The 3-port diverter valve is normally allowing water from the boiler into the HW cylinder, when the cylinder stat is satisfied the 3-port valve gets a supply and opens up the heating port (A) and shuts off the HW port (B). However, the cylinder thermostat was permanently closed so the heating didn't come on. I thought it a bit odd that the timer and the cylinder stat were both no good.
I replaced the cylinder stat, its a type that goes into a pocket on the side of the cylinder. Its a Honeywell Aquastat with no external controls and a temperature range of 70 - 140 C with a dial inside the cover (no over temperature cut-out). I fitted that and left it at the lowest setting as per the previous unit. It fired up, got to temperature and went off I turned up the room stat and the valve opened and the heating came on. It all seemed fine, so off I went.
Got a call the next morning saying that the everything was OK except the shower ran out of hot water after about a minute. It has previously worked fine before the breakdown. I thought I would turn up the cylinder stat a bit, so I did and the pump start sending the boiler water into the cylinder but it didn't last long and turned off. I thought it couldn't have increased the water temperature that quick? As an experiment I turned it up a bit more but the same again. Anyway I left it overnight, the occupant said it was not much better the next day. As an experiment I cut out some of the insulation on the cylinder (it the foam covered type) and fitted a strap on cylinder stat and this seemed to operate as you would expect. So now I am wondering if the probe type stat I fitted is not calibrated correctly, but that seems a bit of a coincidence. I have read that this type of stat is not considered suitable but I thought it would be ok for one night. I set it at 60 degrees C. They phoned the following day to say it was better but still didn't last long enough in the shower. I'm not sure why the surface cylinder stat is not considered suitable but I was thinking of setting it at 70 degrees C for tonight to check for an improvement?
Any thoughts would be much appreciated. I wasn't sure how or why the probe stat wasn't working properly but I suppose it could be just faulty, but it seems odd that the programmer went kaput, and the last cylinder stat and now this one seems to switch off early?