I have a Siemens CU fitted with an 80A/30mA RCCB that covers the whole ring main & cooker.
A couple of nights back there was a bang like a power supply letting go & the RCCB tripped. The bang seemed to come from the general direction of the kitchen but I can't be sure. No physical evidence or nasty smells so I reset the RCCB. All appliances in there appeared to still be working, as was everything else in the house.
Next day it tripped again without any bangs but couldn't be reset. I systematically unplugged everything & kept trying. Last two things (it's always the last right?) were the dishwasher & washing machine. After they were disconnected I could reset the RCCB. Plugged them back in one at a time, the RCCB didn't trip & both devices appeared to be functioning.
I left the WM disconnected & connected DW via a plug-in breaker, also rated at 30mA. Next day the CU RCCB tripped again & the breaker on the DW had also tripped. The DW as idle at this point so it looked like a fault with the DW. Except I reset everything & ran a cycle on the DW & it completed without incident!
So I guess I need to strip the DW out & check around for any signs of what caused the bang. But I'm confused as to how it's still working & tripping the RCCB is only intermittent?
Last time I had anything like this was many years ago when an iron turned out to be the culprit. I just put that down to the mains cable likely breaking down with the constant flexing. But the DW hasn't moved in the 10 years since the kitchen was refurbed.
A couple of nights back there was a bang like a power supply letting go & the RCCB tripped. The bang seemed to come from the general direction of the kitchen but I can't be sure. No physical evidence or nasty smells so I reset the RCCB. All appliances in there appeared to still be working, as was everything else in the house.
Next day it tripped again without any bangs but couldn't be reset. I systematically unplugged everything & kept trying. Last two things (it's always the last right?) were the dishwasher & washing machine. After they were disconnected I could reset the RCCB. Plugged them back in one at a time, the RCCB didn't trip & both devices appeared to be functioning.
I left the WM disconnected & connected DW via a plug-in breaker, also rated at 30mA. Next day the CU RCCB tripped again & the breaker on the DW had also tripped. The DW as idle at this point so it looked like a fault with the DW. Except I reset everything & ran a cycle on the DW & it completed without incident!
So I guess I need to strip the DW out & check around for any signs of what caused the bang. But I'm confused as to how it's still working & tripping the RCCB is only intermittent?
Last time I had anything like this was many years ago when an iron turned out to be the culprit. I just put that down to the mains cable likely breaking down with the constant flexing. But the DW hasn't moved in the 10 years since the kitchen was refurbed.