timer position for an Immersion Heater

Joined
8 Mar 2003
Messages
362
Reaction score
5
Location
Cornwall
Country
United Kingdom
where would an immersion heater timer be positioned if i wanted it in the kitchen?eg. a 16A MCB in the CU, 2.5mm cable to a 20A DP switch then the timer then 2.5 cable to the airing cupboard then an isolating 20A DP switch connected to the imm. heater by heat resistant 2.5(20A) cable?
 
Sponsored Links
sounds like a fine plan to me

just keep it away from the sink
 
You still need DP isolation. Two ways only switch the live. Think this idea though good would be confusing.
 
Sponsored Links
securespark said:
You still need DP isolation. Two ways only switch the live. Think this idea though good would be confusing.

well then you could just use another DP switch to provide that facility. Although i think you might be right about the confusing ideas. I'll shut up now....
 
chris rogers, you're not that news reader chappie are you?
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top