Right, I've changed my CU for my assessment & I thought today I would test it all. Managed to get rid of the missus & kids for the day. I started off by turning all the power off then unplugging everything & then taking all the lightbulbs out. Started with the continuity of protective conductors on the lighting circuit by putting the brown wire into the earth bar & went about checking continuity at the ceiling points. Suprisingly, found that upstairs never had any continuity & there was no earth. Managed to put another earth in around the loft which was a nightmare & took ages cause I didnt want to bodge it & our loft is full. All tested & ok.
Then I tested r1, r2 & rn on the ring circuit & that seemed ok
Next I connected the phase & neutral together (incoming & outgoing) & went round each socket with a plug in thing that you can plug your meter into. Results seemd to be within 0.1 ohms of each other except for the spurs. Then I connected phase & cpc together & went around the sockets again. The results seemd to be approx 0.1 - 0.2 ohms more than the previous test, the OSG says these results should be substantially the same, is this ok ?
Then I went onto insulation test & seemed to be getting very random results. Do I have to disconnect the wires from the cb, neutral & earth bar before doing these tests or can they be left connected ?
Then the phone went & the missus & kids wanted to come home so that was that & I didnt seem to get a lot done in the end.