Hi All
Just wondered whether anyone has expereinced this problem?
Our Trianco Eurostar outside boiler started to lock out on its first morning start, although not every morning. Once the santronic lock out was reset it fired up and ran fine all day. To get by I added an early morning (4am) additional timer slot so it was not switched off for as long, which helped.
However this morning with an outside temperature of -5 it locked out and would not start at all, just timing out on each reset I also spotted a damp patch of oil under the burner. Motor and fan run up each time and some ignition is heard before lock out.
What seems to be happening is the nozzle is dripping oil into the burner, and I suspect overfueling so the photo cell doesn't sees a clean burn when starting up.
I am hoping a new pump c/w solenoid valve will cure the fault?
I have also checked:
All oil filters and oil lines, (oil lines replaced as originally thought leak causing drain back).
Danfoss pump, filter clean and turns freely
Cleaned and tested photocell
Adjusted electrodes checked spark.
Replaced nozzle (with one changed last service so should be ok)
One thing that does puzzle me is that I tried to fool the photcell by holding it on a torch, but the burner still locks out. Perhaps the photo cell needs more intense light? (I was hoping to get the burner to burn off the excess fuel and run for a while so we could have some heat)
Any thoughts?
Just wondered whether anyone has expereinced this problem?
Our Trianco Eurostar outside boiler started to lock out on its first morning start, although not every morning. Once the santronic lock out was reset it fired up and ran fine all day. To get by I added an early morning (4am) additional timer slot so it was not switched off for as long, which helped.
However this morning with an outside temperature of -5 it locked out and would not start at all, just timing out on each reset I also spotted a damp patch of oil under the burner. Motor and fan run up each time and some ignition is heard before lock out.
What seems to be happening is the nozzle is dripping oil into the burner, and I suspect overfueling so the photo cell doesn't sees a clean burn when starting up.
I am hoping a new pump c/w solenoid valve will cure the fault?
I have also checked:
All oil filters and oil lines, (oil lines replaced as originally thought leak causing drain back).
Danfoss pump, filter clean and turns freely
Cleaned and tested photocell
Adjusted electrodes checked spark.
Replaced nozzle (with one changed last service so should be ok)
One thing that does puzzle me is that I tried to fool the photcell by holding it on a torch, but the burner still locks out. Perhaps the photo cell needs more intense light? (I was hoping to get the burner to burn off the excess fuel and run for a while so we could have some heat)
Any thoughts?