I have a somewhat odd radial circuit serving one side of a kitchen - circuit diagram below (sorry if it strains the eyesight). I'd appreciate some expert (constructive) advice on the best way to remove the potential overload.
Although, AIUI, the 32A MCB is suitable for the runs of [edit]2 x[/edit] 2.5mm and 4mm, the circuit then continues in single 2.5mm and is overloaded if all the high load appliances potentially connected are drawing power at the same time. This is, to be honest, quite likely. The washing machine takes quite a battering in a family of five and the tumble dryer is quite likely to be on at the same time. And the steam generator/iron is kept busy as well.
Clearly, one option is to downrate the MCB to 20A but that's not going to take the load of w/machine and dryer together so will keep tripping. My best idea so far is to take separate feeds from the first connection unit (where the 4mm run ends) to the existing w/machine and dryer FCUs and take the onward feed through a 13A FCU so protecting the rest of the 2.5mm circuit. This means that the high load appliances would be drawing through the 2 x 2.5mm/4mm runs of cable and I can live with limit of 13A on the rest of the circuit. The new cable runs would have to be on the surface, likewise the new FCU for the rest of the circuit, but that's bearable because they'll be tucked behind the machines.
I understand that the feeds to the FCU should ideally be in 4mm but I'm unsure about physical viability of terminating 2 x 4mm conductors. As that part of the cable will be protected anyway by the 13A fuse, would it be OK to run them in 2.5mm?
Hope this makes some sense and looking forward to comments.
Thanks to ImageShack for Free Image Hosting
Although, AIUI, the 32A MCB is suitable for the runs of [edit]2 x[/edit] 2.5mm and 4mm, the circuit then continues in single 2.5mm and is overloaded if all the high load appliances potentially connected are drawing power at the same time. This is, to be honest, quite likely. The washing machine takes quite a battering in a family of five and the tumble dryer is quite likely to be on at the same time. And the steam generator/iron is kept busy as well.
Clearly, one option is to downrate the MCB to 20A but that's not going to take the load of w/machine and dryer together so will keep tripping. My best idea so far is to take separate feeds from the first connection unit (where the 4mm run ends) to the existing w/machine and dryer FCUs and take the onward feed through a 13A FCU so protecting the rest of the 2.5mm circuit. This means that the high load appliances would be drawing through the 2 x 2.5mm/4mm runs of cable and I can live with limit of 13A on the rest of the circuit. The new cable runs would have to be on the surface, likewise the new FCU for the rest of the circuit, but that's bearable because they'll be tucked behind the machines.
I understand that the feeds to the FCU should ideally be in 4mm but I'm unsure about physical viability of terminating 2 x 4mm conductors. As that part of the cable will be protected anyway by the 13A fuse, would it be OK to run them in 2.5mm?
Hope this makes some sense and looking forward to comments.
Thanks to ImageShack for Free Image Hosting