madonna said:
Thanks for the prompt reply.
Firstly the repair was with a terminal block but i dont know at what rate other than it being a standard small size. It was then taped over and a thick filler covered over.
1) There is no such thing as a "standard small size". There are several sizes, and if you don't know what rating you've used then you've been very sloppy, possibly dangerous. The fact that you think it's a small one is worrying.
2) You should not have used a terminal block at all - if the joint is inaccessible it must be crimped or soldered - screw connections are unacceptable.
3) Tape is not adequate protection for choc-block.
4) Tape is not waterproof if you're going to use plaster/filler.
The cable i drilled thru was leading to a 13amp socket.You say this is usually protected by a 30/32 breaker.I have a 16amp in.
2.5mm² radial? Just the one socket? Is the cable in one of the permitted zones? If yes, WTF were you drilling there, if no, who installed it?
the trip happens when the washer ,dryer and kettle are used together.
But not when used seperatly. one at a time.
1) I'm not surprised - that lot adds up to more than 16A. Don't see why your awful bodged repair should make a difference though.
2) How do you manage to use 3 appliances at the same time from one socket? (Did you know, BTW, that sockets are only rated at 13A?)
3) Is it the 16A MCB that's tripping, or the RCD?