Every time I seem to have a solution to routing cable from the CU to a newly sited single oven and combination microwave, there is a setback.
The latest problem is that the Ashley & Rock CU, despite its modern specification is no longer made, or catered for in terms of mcb's.
After much searching I think I have found substitute mcb's, but need to check that my calculations are correct before I order them, and waste money.
The pyrolitic oven max load is 3.5 kw. Electrolux state a 16 amp fuse.
The combination MW is 3.4 kw and they state a 15 amp fuse (although originally I was mistakenly told 13 amp).
I am now proposing a 10 metre run of 2.5 mm cable for each radial, with 2 x 16 amp mcb's in the CU. I can't get a 15 amp mcb.
The cabling will run partly through plastic conduit, stud and plasterboard partitioning, and under a chipboard floor.
Should I up the cable to 4mm or 6mm? Is it OK to use the 16 amp mcb
for the microwave? I calculate the load to be 14.78 amps.
Thanks
The latest problem is that the Ashley & Rock CU, despite its modern specification is no longer made, or catered for in terms of mcb's.
After much searching I think I have found substitute mcb's, but need to check that my calculations are correct before I order them, and waste money.
The pyrolitic oven max load is 3.5 kw. Electrolux state a 16 amp fuse.
The combination MW is 3.4 kw and they state a 15 amp fuse (although originally I was mistakenly told 13 amp).
I am now proposing a 10 metre run of 2.5 mm cable for each radial, with 2 x 16 amp mcb's in the CU. I can't get a 15 amp mcb.
The cabling will run partly through plastic conduit, stud and plasterboard partitioning, and under a chipboard floor.
Should I up the cable to 4mm or 6mm? Is it OK to use the 16 amp mcb
for the microwave? I calculate the load to be 14.78 amps.
Thanks