I recently moved into a mid 50's 2 bedroom bungalow and I'm having issues with the heating and would be grateful for some advice.
I am unable to balance the radiators to give a temperature differential of anything greater than 1 to 5 degrees across the rads and 4 to 8 degrees across the boiler after the system has been running for an hour or so with the boiler output set at 70 degrees and all the TRV's heads removed. The lock shields are open from. The only way I can get the boiler return temperature down to 55 degrees or lower is to turn the boiler heating output down to 60 degrees or lower.
I've read different things on different websites which have left me somewhat confused but have established that the problem could be caused by any or all of the following:
There are 3 different makes of lock shield with 3 different number of turns from fully open to fully closed. They are open from 1/2 turn to 5/8 turn.
Any advice would be much appreciated in particular regarding the pump speed and whether the boiler is too big.
I have a drawing detailing building layout, room sizes, windows, pipe runs and sizes etc which I can post if it would help.
I am unable to balance the radiators to give a temperature differential of anything greater than 1 to 5 degrees across the rads and 4 to 8 degrees across the boiler after the system has been running for an hour or so with the boiler output set at 70 degrees and all the TRV's heads removed. The lock shields are open from. The only way I can get the boiler return temperature down to 55 degrees or lower is to turn the boiler heating output down to 60 degrees or lower.
I've read different things on different websites which have left me somewhat confused but have established that the problem could be caused by any or all of the following:
- Blockages/air in system
- Poor balancing of the radiators
- Lock shield open too much
- Pump speed too high
- Boiler output to high
- The heating system has a Glowworm 30cxi boiler with 6 radiators.
- The boiler manual states a maximum of 20 degs boiler differential at maximum heating output of about 82 degs but it doesn't give figures at other temperatures.
- Ideal temperature drop across radiators about 11 degrees
- Ideal heating output temperature about 70 to 75 degrees
- The bungalow is about 724 sqft/67 sqm.
- The external wall cavities are insulated with 75mm blown fibre.
- The windows and external doors are double glazed with 20-25mm gaps
- The system was cleaned, flushed and refilled with new inhibitor and there are no cold spots on the radiators
- The heat exchanger, expansion and condensate tanks were also replaced
There are 3 different makes of lock shield with 3 different number of turns from fully open to fully closed. They are open from 1/2 turn to 5/8 turn.
Any advice would be much appreciated in particular regarding the pump speed and whether the boiler is too big.
I have a drawing detailing building layout, room sizes, windows, pipe runs and sizes etc which I can post if it would help.