I've had electrical underfloor heating in the bathroom for 4 years and its been working perfectly. We went away for a couple of days and I set the Devireg touch to holiday mode so that it would come on when we got back. When we returned the RCD that supplies the underfloor heating (and the freezer!!) had tripped. Once I'd established that it was the UFH that was the problem, I did some simple testing with a Fluke 117:
Resistance of mat 69.6 Ω
Resistance of one leg of mat to earth 67.1Ω
Resistance of second leg of mat to earth 6.4Ω
Measurement taken from the controller - wires disconnected and using earth fed from mains and connected to earthing terminal on back box. There is no earthing connection on controller.
I assume the measurement to earth should be virtually ∞ (Infinity) - or certainly thousands of Mega-ohms.
Am I missing something or does this mean there is a short to earth somewhere on the mat close to the controller.
If so then any idea how to locate it to a single tile - forever hopeful.......
Resistance of mat 69.6 Ω
Resistance of one leg of mat to earth 67.1Ω
Resistance of second leg of mat to earth 6.4Ω
Measurement taken from the controller - wires disconnected and using earth fed from mains and connected to earthing terminal on back box. There is no earthing connection on controller.
I assume the measurement to earth should be virtually ∞ (Infinity) - or certainly thousands of Mega-ohms.
Am I missing something or does this mean there is a short to earth somewhere on the mat close to the controller.
If so then any idea how to locate it to a single tile - forever hopeful.......