Just after a sanity check. Replaced the EV at the weekend, water coming out of the valve at the top. Drip still present in the tundish drain. Confirmed it's not the boiler or tank PTRV, it's coming from the combination valve unit PRV. Before I replace the PRV, I'm unsure that the EV is in the right place. The system was installed by a professional in 2011. I understand the EV has to sit on the cold supply to absorb any expansion and back pressure to the mains, however if the combi valve unit has a check valve installed, and I think it has, the expanding water won't get to the EV in this current set up.
Appreciate any advice here.