I've looked in the current threads and not found the answer to my question, but apologies if it HAS been answered and I haven't seen it.
For the avoidance of doubt I won't be carrying out any work myself.
Here goes .... I've read through the G3 regulations (with regard to the D2 pipe) and also numerous items of advice regarding pipe size, pipe material, the fall on the pipe, sleeving it through walls, the 300mm drop required below the tundish etc.
But I haven't seen any reference to this set of circumstances :-
If I base my run on 8 metres from the tundish to the point of discharge outside, and the installer uses 6 x elbows or bends and uses 22mm copper pipe I get the calculation as follows.:-
9 metres max, less 6 x elbows or bends @ 0.8m each = 6 x 0.8m equals 4.8 m
9 metres less 4.8 metres equals 4.2 metres.
And as my run is 8 metres the installer can't use 22mm pipe.
-------------------------------------------------------
That means he would need to move up to 28mm pipe, in which case there's plenty spare capacity as 28mm pipe allows for an 18 metre run and if I subtract the 6 bends (at 1x metre per bend) I have capacity for 12 metres ... and I only need 8.
-------------------------------------------------------
My question is .... can the installer come away from the tundish in 28mm and run the bulk of the route in 28mm - but reduce down to 22mm for the last, say, 3 metres?
The only reason I ask is I'm planning the logistics of the route through my bathroom and garage and the last couple of metres would be easier to run in 22mm. To be honest I'm not clever enough to work out exactly what the total resistance figure would be by mixing two different sizes of pipe but I'm hazarding a guess by reducing down from 28mm to 22mm for the last couple of metres and assuming it would comply with regs.
On the other hand it might be that it's not permitted to mix sizes - but I can't see it written down anywhere..
Ta.
For the avoidance of doubt I won't be carrying out any work myself.
Here goes .... I've read through the G3 regulations (with regard to the D2 pipe) and also numerous items of advice regarding pipe size, pipe material, the fall on the pipe, sleeving it through walls, the 300mm drop required below the tundish etc.
But I haven't seen any reference to this set of circumstances :-
If I base my run on 8 metres from the tundish to the point of discharge outside, and the installer uses 6 x elbows or bends and uses 22mm copper pipe I get the calculation as follows.:-
9 metres max, less 6 x elbows or bends @ 0.8m each = 6 x 0.8m equals 4.8 m
9 metres less 4.8 metres equals 4.2 metres.
And as my run is 8 metres the installer can't use 22mm pipe.
-------------------------------------------------------
That means he would need to move up to 28mm pipe, in which case there's plenty spare capacity as 28mm pipe allows for an 18 metre run and if I subtract the 6 bends (at 1x metre per bend) I have capacity for 12 metres ... and I only need 8.
-------------------------------------------------------
My question is .... can the installer come away from the tundish in 28mm and run the bulk of the route in 28mm - but reduce down to 22mm for the last, say, 3 metres?
The only reason I ask is I'm planning the logistics of the route through my bathroom and garage and the last couple of metres would be easier to run in 22mm. To be honest I'm not clever enough to work out exactly what the total resistance figure would be by mixing two different sizes of pipe but I'm hazarding a guess by reducing down from 28mm to 22mm for the last couple of metres and assuming it would comply with regs.
On the other hand it might be that it's not permitted to mix sizes - but I can't see it written down anywhere..
Ta.