Unvented cylinder over pressure

Joined
4 Jan 2009
Messages
6,019
Reaction score
610
Location
Herefordshire
Country
United Kingdom
I have a fairly new unvented cylinder.

About 6 months ago I noticed a change in behavior of the hot water tap pressure and the gauge reading 3.5 bar (normally 3)

Recently I happened to noticed 8 bar and the turndish dripping.

I've had the installer in to look at it, who hasn't been very helpful.

What could the problem be ?
 
Sponsored Links
The installer!

Edit: I’m not a plumber but it could be the expansion vessel or, and my mum had this, she'd slightly knocked the fill valve lever under the sink so it was constantly pressurising the system.
 
Last edited:
Sponsored Links
Whoever you get to look at it needs to be certified to work on unvented cylinders. Bob
 
Sounds like it just needs the expansion vessel or air gap recharging. Pretty basic stuff for a qualified engineer. When was it last serviced?
 
Last edited:
It really needs looked at by a qualified chap who knows what he's doing. If the installer isn't much help then he doesn't know what he's doing and shouldn't have installed it in the first place. The fact that the cylinder is getting to 8 bar is worrying, the pressure relief valve on the combination valve should have opened @3bar and should be flowing quite significantly @ 8 bar, not just dripping.

Is it a Megaflo? Can you give us pics?
 
A pic of your setup would help, it is unusual to have a pressure gauge on the DHW side ,you will always have a gauge on the primary water side, but on either side 8 Bar is a bit worrying, a pic is worth a thousand words so would be better
 
It’s a Jet tank.
Pressure relief on tank is 10 bar. So that is why that bit is only dripping.

How do you recharge it?

Do U drain the whole tank and then refill.
As that is what he is saying. As well as other things

How often are they meant to be recharged ?
 
Last edited:
I guess you press in the relief valve to open it

The air volume within the cylinder will periodically require recharging to ensure any expanded water is accommodated within the unit. A discharge of water INTERMITTENTLY from the pressure relief valve will indicate the air volume has reduced to a point where it can no longer accommodate the expansion. To recharge the air volume:-
i) Turn off the heat source to the cylinder via programmers / immersion isolation switch(es).

ii) Turn off the water supply to the cylinder by turning off the isolating valve at the cylinder, if fitted or the main incoming supply to the house.

iii) Open the lowest hot tap supplied by the cylinder.

iv) Hold open the temperature and pressure relief valve until water ceases to run from the tap and gurgling noise at the valve stops.

v) Close the temperature and pressure relief valve.

vi) Turn on the water supply to the cylinder

vii) The air volume will be automatically recharged as the unit refills. If after following the above actions water still discharges from the pressure relief valve, further advice should be sought from a competent installer or Technical Support
 
Last edited: