A friend of mine who had a 10L UV cylinder equipped with a Ariston 571730 PRV (like the one in the photo) and he noticed that, from time to time the PRV would have lifted and couldn't figure out what the problem was, he replaced the PRV, same problem, I gave him the loan of a pressure gauge which he attached to the HW outlet, pressure was ~ 2.5bar with a cold cylinder but within 10 minutes or so after the start of reheating the PRV started lifting at 8.5bar, on investigation, he found that the previous owner had installed a NRV on the mains, cylinder located ~ 15/20 meters downstream of this, he obviously removed the NRV, problem solved but noticed that the pressure would still rise by ~ 0.5/0.8bar on reheating. I took the old PRV apart and found it quite interesting, it was/is a combination valve with a PRV, NRV and anti syphon valve, the PRV portion is obviously allways opened to the cylinder, the NRV opens inwards to admit cold water and the anti syphon valve is a "mini" NRV inside the larger NRV but opens outwards, quite clever?, presumably to prevent the whole HW contents draining into the cold mains in the event of the mains supply failing or someone isolating the mains to do some work in the house.