Hello guys, I am trying to figured out the wiring on my current Honeywell Receiver which works fine with my wireless Honeywell CM927.

I am confused with the current wiring of my receiver - please see pictures which I will attach:

current wiring:

N blue cable (I guess neutral)
L brown cable (I guess live)
L brown cable (this is where I get confused as this is a small brown cable connecting A to L like a loop cable)

A small brown cable coming from L as above
B green cable (I guess open wire?)
C empty
D empty
E empty

on my new nest heat link I need to identify the common and open wires from my current setup so I can carry on.

any help would be appreciated.

regards,
Seb.
 

Attachments

  • 349999C7-AB52-4536-8FDE-3E0E96F433CB.jpeg
    349999C7-AB52-4536-8FDE-3E0E96F433CB.jpeg
    300.1 KB · Views: 872
  • 7FB98843-69F6-4DE0-B0AC-536DAC3DD8D5.jpeg
    7FB98843-69F6-4DE0-B0AC-536DAC3DD8D5.jpeg
    167.6 KB · Views: 612
Sponsored Links
One more picture if it helps
 

Attachments

  • 3B1FB289-32A3-4493-8660-911BDC54E4CF.jpeg
    3B1FB289-32A3-4493-8660-911BDC54E4CF.jpeg
    124.5 KB · Views: 665
Couldnt be simpler but never go by wire colours on a heating system

honeywell Nest

N to N
L to L
Link L to 2
C to 3
 
Sponsored Links
If anyone can just confirm what’s the common and open wire on my current system that would be great. I want to make sure I understand current wiring to proceed with the next steps. Thank YOU in advance
 
current wiring:

N blue cable (I guess neutral)
L brown cable (I guess live)
L brown cable (this is where I get confused as this is a small brown cable connecting A to L like a loop cable)

A small brown cable coming from L as above
B green cable (I guess open wire?)
C empty
D empty
E empty
The two L terminals on the Honeywell reciever are linked together internally. The loop from L2 to A means that terminal A always has 240Vac on it. When the switch in the receiver closes terminal B (switched live) provides 240Vac to turn the boiler on.

Terminal C is used for cooling systems.
 
Thank you so much for all the answers, things are starting to get clear in my diagram mind :)

As per what D_Halisham said I will then use the brown cable currently connected to L1 as my common wire and the cable connected to B my open wire, therefore the small brown cable connecting L2 to A can be just removed.

I tried to draw what I will be doing just to confirm if anyone can please confirm it that would be great. I don’t want to try anything before I am 100% as wife already threatened me with a divorce depending on the outcome....



Read more: https://www.diynot.com/diy/threads/...e-from-honeywell-r6660d.537310/#ixzz6BOCMxxGg
 
Drawing of what to do next with wires
 

Attachments

  • A26229C8-7D8E-476F-81EF-2195417FB6F9.jpeg
    A26229C8-7D8E-476F-81EF-2195417FB6F9.jpeg
    131.7 KB · Views: 745
EFLImpudence
thanks a lot for all the spot on info however do you mind clarifying when you said:

N to N
L to L
Link L to 2
€ B to 3


my new Nest Thermostat only requires two cables (Common and Open) therefore N and L1 won’t be used from what I understood - I will use the terminal blocks to isolate them.

Link L to 2 means I will connect L to Common socket on nest?


€ B to 3 means I will connect B to NO socket on nest?


I didn’t understand what numbers 2 and 3 meant on your earlier post. I will post a picture of how Nest thermostat sockets are arranged.






Read more: https://www.diynot.com/diy/threads/...e-from-honeywell-r6660d.537310/#ixzz6BOY4TEru
 

Attachments

  • image.jpg
    image.jpg
    137.4 KB · Views: 782

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top