Got asked to look at fixing a spotlight on one of the machines at work today. Its a 'Dynamic Balancer' used for balancing armatures/rotors and the guy said the spotlight has started blowing the bulbs more often. The light is one of these 'security' lights without the PIR. Anyway as one of the end prongs was badly burnt I decided to look for a loose connection when I discovered the earth from the lamp in the back of the fitting was connected to the neutral of the incoming supply (240v)and vice versa.
Looking further into it I discovered the 240v supply had been picked up from one of the 415v phase supplies and the main incoming earth as there was no neutral.
Now I'm not the hottest on industrial wiring, (I'm an armature winder/electrical fitter), so to me this is totally wrong. Is this a common method though as it was done by the people who installed the safety covers around the machine.
Looking further into it I discovered the 240v supply had been picked up from one of the 415v phase supplies and the main incoming earth as there was no neutral.
Now I'm not the hottest on industrial wiring, (I'm an armature winder/electrical fitter), so to me this is totally wrong. Is this a common method though as it was done by the people who installed the safety covers around the machine.