To do it you would NEED the combi's "CH" side to come on,
as you need the CH pipework up to where you Tee it off with zone valves to be actively heated.
To put it into perspective, a normal system boiler only has "CH" flow and return, unlike a combi's HW in & out, CH Flow & Return.
You add the gubbings to control where the "CH" hot water goes with zone valves on seperate pipe runs to the radiators and cylinder,
the zone valves control where the water can go and external controls tell the boiler when to fire and which valves to operate.
have a look at S or Y plan as suggested, you need to put all the external controls in place (Room thermostat, cylinder stat, timer/programmer) then tell the combi on it's front panel you want CH constantly.
Once both thermostats are satisfied, the boiler will turn off for the CH side.
Add in the programmer so you can say when you want Cylinder HW and/or Heating, once the thermostats tick over, boiler stops heating.
if you turn the "CH" side of the combi off, you'd turn the heating and cylinder heating off.
Pump is built into the combi normally and should be able to handle it,
I'd suggest getting someone competent to design and do the above
Looking at the diagrams provide here
http://wiki.diyfaq.org.uk/index.php?title=Central_Heating_Controls_and_Zoning, its making a bit more sense to me.
I called a few local plumbers today and they didnt seem interested.
Look at the diagrams the Y-plan looks like alot less valves to buy and fit.
Currently I have the ecotec 837 boiler which is controlled by a VRT 392f. Could this still be used, or would I need to replace this?
I understand I need to split the flow and return straight from the boiler before any rads. Add a 3port mid-position valve on the flow side and nothing on the return, jut to ensure its connected as close to the boiler.
When my bathroom and kitchen was done, they piped hot and cold in 15mm. As the units are in the way, I can not upgrade to 22mm. Would it be ok, to change to 22mm as close as possible to the main stop cock (about 1m) from 15mm to feed the tank, and then run 22mm for hot water to the furthest I can get for DHW?