I have a small 3 bed house with Vaillant ecoTec plus 415 boiler feeding a 1980s Y-Plan system with a conventional indirect hot water cylinder and 8mm microbore radiators. There is not (as yet) any control over the water flow rate through the indirect coil (I plan to install a gate valve in the Spring when I change the rads for new ones).
The problem I have is that it takes an age (up to an hour) for the hot water tank to heat up each morning (with rads off). This is with the boiler flow set to 70 deg C and the cylinder stat set to 50 deg C. So this morning I got my watch out and monitored what the boiler got up to. This is what I found:
T=0 Boiler fires up at what sounds like full power. Circulating temperature rapidly rises to 70 deg C.
T=4 Boiler still in S4 mode but with burner running on low maintaining 70 deg C output temperature. Interesting - I didn't realise it could modulate down like that.
T=20 Boiler now in S7 mode (overrun) with burner off and temperature rapidly dropping. Why did it switch out of low power mode?
T=24 Boiler back on at full power for about 1 minute until 70 deg C reached.
T=25 Boiler back to S7 (overrun) and temperature dropping again.
T=30 Boiler back on full power...
The last two states repeat constantly for further 30 minutes or so until eventually the cylinder stat is satisfied. But as the average flow temperature is now so low the cylinder is interminably slow to heat up.
My question is what should I do to correct this? If the boiler can modulate down I would prefer it to stay in that mode but for some reason it switches out and I don't now how to correct this.
Any guidance much appreciated.
The problem I have is that it takes an age (up to an hour) for the hot water tank to heat up each morning (with rads off). This is with the boiler flow set to 70 deg C and the cylinder stat set to 50 deg C. So this morning I got my watch out and monitored what the boiler got up to. This is what I found:
T=0 Boiler fires up at what sounds like full power. Circulating temperature rapidly rises to 70 deg C.
T=4 Boiler still in S4 mode but with burner running on low maintaining 70 deg C output temperature. Interesting - I didn't realise it could modulate down like that.
T=20 Boiler now in S7 mode (overrun) with burner off and temperature rapidly dropping. Why did it switch out of low power mode?
T=24 Boiler back on at full power for about 1 minute until 70 deg C reached.
T=25 Boiler back to S7 (overrun) and temperature dropping again.
T=30 Boiler back on full power...
The last two states repeat constantly for further 30 minutes or so until eventually the cylinder stat is satisfied. But as the average flow temperature is now so low the cylinder is interminably slow to heat up.
My question is what should I do to correct this? If the boiler can modulate down I would prefer it to stay in that mode but for some reason it switches out and I don't now how to correct this.
Any guidance much appreciated.