Hello,
I have a vaillant boiler, the system is filled to approx 1bar.
The filling valves are in the closed position.
When the CH is on, the pressure increases relatively fast, after 15minutes it will have reached approx 80C and 2.5bar, when the CH is turned off, the pressure will return to 1bar (eventually). Water has came out of the PRV sometimes when the CH has been on.
Sounds like could be the expansion vessel but dont want to get someone in to look at it or play with it myself unless someone could confirm (or give a different theory),
Any help would be great,