Hi All, I have a Vaillant ecoTEC 637 plus, likely fitted ~2017 mounted as a system boiler, single zone, with a separate water tank for DHW.
The thermostat is a Salus RT500 wired via the 230v RT connection. There is also a Drayton scheduler.
(Small parenthesis: It is also a classic case of oversized boiler, 37 kw whilst I have maybe 17kw of rads and say 3kw for the cylinder. The technical doc says it can modulate down to 6kw and I did manage to set it at this level in d.0 to try. Trying to make the best of a bad situation by somewhat improving controls)
I learned on this forum about the installer mode and ability to take readings (D40/D41 for flow / return flow) and made tests.
When starting from cold, 12 degrees C outside it does this:
1 - 29 flow temp / 25 return flow, turn on, low flame for 5 minutes
2 - After 5 minutes flame is increased, looks like 75% on the display, water heats up quickly, reaches 67/47 in 7 minutes
3 - Boiler gradually reduces the flame, after 11 minutes it's at 68 / 61, flame down at ~25%
4 - It then stays at 69/63 until the room reaches the set temperature and thermostat tells the boiler to turn off.
My questions:
A) Is it modulating? I thought that only Vaillant digital controls via eBus could modulate, but this is a 230v RT connection on a cheap thermostat?
B) Does this mean that if I replace the thermostat by a smart one (Hive, Tado ..) the boiler will keep modulating in the same way as it does now?
Many Thanks
The thermostat is a Salus RT500 wired via the 230v RT connection. There is also a Drayton scheduler.
(Small parenthesis: It is also a classic case of oversized boiler, 37 kw whilst I have maybe 17kw of rads and say 3kw for the cylinder. The technical doc says it can modulate down to 6kw and I did manage to set it at this level in d.0 to try. Trying to make the best of a bad situation by somewhat improving controls)
I learned on this forum about the installer mode and ability to take readings (D40/D41 for flow / return flow) and made tests.
When starting from cold, 12 degrees C outside it does this:
1 - 29 flow temp / 25 return flow, turn on, low flame for 5 minutes
2 - After 5 minutes flame is increased, looks like 75% on the display, water heats up quickly, reaches 67/47 in 7 minutes
3 - Boiler gradually reduces the flame, after 11 minutes it's at 68 / 61, flame down at ~25%
4 - It then stays at 69/63 until the room reaches the set temperature and thermostat tells the boiler to turn off.
My questions:
A) Is it modulating? I thought that only Vaillant digital controls via eBus could modulate, but this is a 230v RT connection on a cheap thermostat?
B) Does this mean that if I replace the thermostat by a smart one (Hive, Tado ..) the boiler will keep modulating in the same way as it does now?
Many Thanks