Scratching my head here.
Boiler is fitted down stair , heating is fine.
Down stairs Kitchen DHW works fine.
Upstairs sinks and shower are cold
Upstairs bath is hot..
When upstairs sink tap or shower is turn to hot the white lever on the diverter valve moves slightly but not enough to depress the micro switch. Note: This operates correctly for the kitchen.
The diverter valve is fairly new and has been replaced twice during the life of the boiler.
The heat exchanger has never been replaced, and I am feeling this may be the cause of the problem restricting flow such that the upstairs is the first to see the failure. Prior to this failure I have experienced showers which fluctuate hot warm which I understand can also point to heat exchangers.
I wanted to run my logic past some experts before I spend £140+.
I have measured flows rates at various points:
Downstairs
Cold tap kitchen: 10.5 l/min
Hot tap kitchen: 8.4 l/min
Upstairs
Cold tap bath: 10.4 l/min
Hot tap bath: 7.2 l/min
Cold sink: 7.2 l/min
Hot sink: 4.8 l/ min
Shower flows seems to be closer to bath but still not sufficient to demand DHW.
The flow reduction upstairs (between bath & sink) seems to be consistent and at ~ 30% - good or bad I'm not sure. Note: Plastic pipe is used for all house plumbing.
Interestingly, if sink and shower turned to hot at the same time the boiler will fire up.
Any help gratefully received,
Jim
Boiler is fitted down stair , heating is fine.
Down stairs Kitchen DHW works fine.
Upstairs sinks and shower are cold
Upstairs bath is hot..
When upstairs sink tap or shower is turn to hot the white lever on the diverter valve moves slightly but not enough to depress the micro switch. Note: This operates correctly for the kitchen.
The diverter valve is fairly new and has been replaced twice during the life of the boiler.
The heat exchanger has never been replaced, and I am feeling this may be the cause of the problem restricting flow such that the upstairs is the first to see the failure. Prior to this failure I have experienced showers which fluctuate hot warm which I understand can also point to heat exchangers.
I wanted to run my logic past some experts before I spend £140+.
I have measured flows rates at various points:
Downstairs
Cold tap kitchen: 10.5 l/min
Hot tap kitchen: 8.4 l/min
Upstairs
Cold tap bath: 10.4 l/min
Hot tap bath: 7.2 l/min
Cold sink: 7.2 l/min
Hot sink: 4.8 l/ min
Shower flows seems to be closer to bath but still not sufficient to demand DHW.
The flow reduction upstairs (between bath & sink) seems to be consistent and at ~ 30% - good or bad I'm not sure. Note: Plastic pipe is used for all house plumbing.
Interestingly, if sink and shower turned to hot at the same time the boiler will fire up.
Any help gratefully received,
Jim