Firstly apologies for the long 1st post!
I have recently had an ecoTec Plus 428 installed with the VRC 430 weather compensator. I am having problems with the boiler constantly going into anti-cycling mode and not maintaining the required target flow temperature for more than a few seconds. Our installer didn't seem to understand the system at all well, so I'm hoping somebody can help with this issue.
The boiler appears to behave correctly when central heating is first demanded, heating to the target flow temperature issued from the VRC 430 for around 5 to 10 minutes. When the VRC 430 (which is wall mounted in the hallway) registers an increase in the room temperature and adjusts the flow temperature downwards, then the boiler seems to go into a permanent cycle as follows (VRC 430 set to 25C target room temp, actual room temp is 21.5C, outside temp 16C, heating curve 1.8, central heating set to Manual, water set to Off):
Target flow rate demanded by VRC 430 is 57C, confirmed on boiler via d.5
1. The radiator symbol on the boiler begins flashing. Status code is S.7. Flow temperature begins to drop from 57C to 43C, return temp is 43C. d.67 shows remaining anti-cycling time at 7 mins.
2. After 5 mins the pump overrun time expires (d.1 set at the default 5 mins). Status code changes to S.8. d.67 shows 2 mins remaining anti-cycling time.
3. After the anti-cycling time expires the radiator symbol stops flashing. Status code changes to S.2.
4. After approximately 15 seconds burner symbol shows, gas valve symbol shows. Status code changes to S.3.
5. After approximately 5 seconds status code changes to S.4, flow temperature increases from 43C to 57C over approximately 30 seconds.
6. Flow temperature reaches 57C/58C. After no more than around 5 seconds (sometimes less) radiator symbol begins flashing, burner symbol disappears, gas valve symbol disappears. Status code changes to S.5, flow temperature begins falling.
7. After around 10 seconds status code changes to S.7.
8. Cycle begins at 1 again.
Once this cycle has begun, it seems to continue indefinately with the boiler only reaching the target flow temperature of 57C for a 5 second maximum every 8 to 10 minutes. Clearly with this cycle the radiators cool, and the target temperature of 25C is never reached, in fact it never rises above 21.5C.
Setting d.2 to a smaller number (2 mins) decreases the time to complete the above cycle, but has no other effect on the cycle. Also setting d.1 to a smaller number (2 mins) only reduces the time that S.7 status code is shown, other than that has no effect on the above cycle. Setting d.0 to a smaller number (5kW-Max) appears to have no effect on the above cycle.
All other boiler parameters are all set to default values with the exception of d.70 which is set to 1=Centre Position.
I have tried changing the Room Temp Control setting of the VRC 430 between Off/Thermostatic/Modulating and it appears to have no effect, other than changing the target flow temperature. The above cycle still takes place. AUTO_OFF on the VRC 430 is set to ECO. Min Flow temp is set to default 15C.
I have also observed on a number of occasions when the boiler goes into the above cycle, the target flow temp suddenly changes to 0C. This causes the heating demand from the VRC 430 to be lost, boiler status goes to S.31. Displayed flow temp on the VRC 430 is then shown to be 0C, even though nothing has changed and there should be a heat demand. The only way to get the system to recover from this appears to be changing the heating curve. Upon setting the curve away from 1.8 then back to 1.8, a target flow of 57C is restored and the above cycle continues.
Circulation pump is Grundfos 15-50, changing the pump speed between the 3 available settings appears to have no effect.
Hot water and heating knobs are both set to maximum, as specified in the instructions for when using a VRC 430.
Pump seems to run as and when requested by the boiler, 3 port valve moves to the correct position controlled via VR 65 control unit.
This is driving me mad, surely it's not supposed to behave like this
Thanks!
I have recently had an ecoTec Plus 428 installed with the VRC 430 weather compensator. I am having problems with the boiler constantly going into anti-cycling mode and not maintaining the required target flow temperature for more than a few seconds. Our installer didn't seem to understand the system at all well, so I'm hoping somebody can help with this issue.
The boiler appears to behave correctly when central heating is first demanded, heating to the target flow temperature issued from the VRC 430 for around 5 to 10 minutes. When the VRC 430 (which is wall mounted in the hallway) registers an increase in the room temperature and adjusts the flow temperature downwards, then the boiler seems to go into a permanent cycle as follows (VRC 430 set to 25C target room temp, actual room temp is 21.5C, outside temp 16C, heating curve 1.8, central heating set to Manual, water set to Off):
Target flow rate demanded by VRC 430 is 57C, confirmed on boiler via d.5
1. The radiator symbol on the boiler begins flashing. Status code is S.7. Flow temperature begins to drop from 57C to 43C, return temp is 43C. d.67 shows remaining anti-cycling time at 7 mins.
2. After 5 mins the pump overrun time expires (d.1 set at the default 5 mins). Status code changes to S.8. d.67 shows 2 mins remaining anti-cycling time.
3. After the anti-cycling time expires the radiator symbol stops flashing. Status code changes to S.2.
4. After approximately 15 seconds burner symbol shows, gas valve symbol shows. Status code changes to S.3.
5. After approximately 5 seconds status code changes to S.4, flow temperature increases from 43C to 57C over approximately 30 seconds.
6. Flow temperature reaches 57C/58C. After no more than around 5 seconds (sometimes less) radiator symbol begins flashing, burner symbol disappears, gas valve symbol disappears. Status code changes to S.5, flow temperature begins falling.
7. After around 10 seconds status code changes to S.7.
8. Cycle begins at 1 again.
Once this cycle has begun, it seems to continue indefinately with the boiler only reaching the target flow temperature of 57C for a 5 second maximum every 8 to 10 minutes. Clearly with this cycle the radiators cool, and the target temperature of 25C is never reached, in fact it never rises above 21.5C.
Setting d.2 to a smaller number (2 mins) decreases the time to complete the above cycle, but has no other effect on the cycle. Also setting d.1 to a smaller number (2 mins) only reduces the time that S.7 status code is shown, other than that has no effect on the above cycle. Setting d.0 to a smaller number (5kW-Max) appears to have no effect on the above cycle.
All other boiler parameters are all set to default values with the exception of d.70 which is set to 1=Centre Position.
I have tried changing the Room Temp Control setting of the VRC 430 between Off/Thermostatic/Modulating and it appears to have no effect, other than changing the target flow temperature. The above cycle still takes place. AUTO_OFF on the VRC 430 is set to ECO. Min Flow temp is set to default 15C.
I have also observed on a number of occasions when the boiler goes into the above cycle, the target flow temp suddenly changes to 0C. This causes the heating demand from the VRC 430 to be lost, boiler status goes to S.31. Displayed flow temp on the VRC 430 is then shown to be 0C, even though nothing has changed and there should be a heat demand. The only way to get the system to recover from this appears to be changing the heating curve. Upon setting the curve away from 1.8 then back to 1.8, a target flow of 57C is restored and the above cycle continues.
Circulation pump is Grundfos 15-50, changing the pump speed between the 3 available settings appears to have no effect.
Hot water and heating knobs are both set to maximum, as specified in the instructions for when using a VRC 430.
Pump seems to run as and when requested by the boiler, 3 port valve moves to the correct position controlled via VR 65 control unit.
This is driving me mad, surely it's not supposed to behave like this
Thanks!