Hello all,
I have moved into my new house which has a Vaillant Ecotec Plus 832. DHW is fine but I just need to confirm the CH is behaving correctly as I couldn't see any other posts with this issue.
The Honeywell CM907 wired room stat calls for heat,
Boiler fires up, burner at full 2 seconds then reduces right down to near minimum,
Target temp climbs very slowly until 5 mins has passed,
Then burner modulates up and target temp of 60 degrees is achieved within a few minutes, and modulates down and keeps stable target temp of 60.
Once the room stat has reached my target of 22, it will then cycle the boiler to keep the temp stable.
But when it calls for heat, the CH temp is only 45 degrees with the burner low, and the burner doesn't increase until the 5 minute delay, then it would modulate up and reach target temp BUT before that happens, the room stat clicks off again.
Repeat cycle but target temp is never achieved again unless the room stat is calling for heat longer than 5 mins (if I increase temp above PB of room stat)
I have checked through other posts and have put some relevant info below to help.
In the menus
Partial load is set to 15kw
Pump over run 5 mins
Pump speed auto
Anti cycle 20mins
System on 8mm microbore
All rads do get hot at the same time after the 5 minutes have elapsed.
Once the system has been running, target 60 and return 54
Is this normal behaviour because the room stat is clicking alot and the rads are barley luke warm, ocassionly the room stat will drop below the target by 0.5 degrees because the flow target temp doesn't get much of a chance to get there within a 5 min burn.
Room stat increase minimum on time to 5 mins max.
5 is the magic number
Thanks in advance
I have moved into my new house which has a Vaillant Ecotec Plus 832. DHW is fine but I just need to confirm the CH is behaving correctly as I couldn't see any other posts with this issue.
The Honeywell CM907 wired room stat calls for heat,
Boiler fires up, burner at full 2 seconds then reduces right down to near minimum,
Target temp climbs very slowly until 5 mins has passed,
Then burner modulates up and target temp of 60 degrees is achieved within a few minutes, and modulates down and keeps stable target temp of 60.
Once the room stat has reached my target of 22, it will then cycle the boiler to keep the temp stable.
But when it calls for heat, the CH temp is only 45 degrees with the burner low, and the burner doesn't increase until the 5 minute delay, then it would modulate up and reach target temp BUT before that happens, the room stat clicks off again.
Repeat cycle but target temp is never achieved again unless the room stat is calling for heat longer than 5 mins (if I increase temp above PB of room stat)
I have checked through other posts and have put some relevant info below to help.
In the menus
Partial load is set to 15kw
Pump over run 5 mins
Pump speed auto
Anti cycle 20mins
System on 8mm microbore
All rads do get hot at the same time after the 5 minutes have elapsed.
Once the system has been running, target 60 and return 54
Is this normal behaviour because the room stat is clicking alot and the rads are barley luke warm, ocassionly the room stat will drop below the target by 0.5 degrees because the flow target temp doesn't get much of a chance to get there within a 5 min burn.
Room stat increase minimum on time to 5 mins max.
5 is the magic number
Thanks in advance