I attended this boiler last week and cleaned the plate HE as it was seriously blocked.
DHW is now working fine and the system pressure is 1.5 bar. The pump is OK and the impeller clean.
However the client reports its giving occasional F22 errors.
If I recall correctly this error is deduced by temperature sensors on flow and return of the primary HE being outside the allowable range preset.
I have previously found this is apparently caused by the two NTCs testing for resistance OK but presumably not having adequately matched curves. This often occurs following dry firing. Replacing them with new sensors usually solves the problem.
Does anyone have experience of other causes of random F22 errors ?
Do I correctly remember that these are dry pocket? If so then does lack of heat transfer paste ever cause this?
Tony
DHW is now working fine and the system pressure is 1.5 bar. The pump is OK and the impeller clean.
However the client reports its giving occasional F22 errors.
If I recall correctly this error is deduced by temperature sensors on flow and return of the primary HE being outside the allowable range preset.
I have previously found this is apparently caused by the two NTCs testing for resistance OK but presumably not having adequately matched curves. This often occurs following dry firing. Replacing them with new sensors usually solves the problem.
Does anyone have experience of other causes of random F22 errors ?
Do I correctly remember that these are dry pocket? If so then does lack of heat transfer paste ever cause this?
Tony