Any advice on this problem Id really appreciate.
Friends Vaillant Sine stopped working. He had 2 plumbers round saying the boiler needed to be replaced for wrong reasons (ignitor not working no parts availalbility) etc.
Ignitor worked fine, but i found the overheat switch open circuit, so i pushed the black knob in and it started to work agaiin for DHW.
When the central heating button gets clicked though the boiler fires up for about 15 seconds, initially full rate, then half rate, then it cuts out.
I checked the signals to the pump and they run when ch is on.
Hot water seems to be being circulated around the inner boiler but not to the central heating circuit.
If I remove the nTc purple wire it fires up fine, but still doesnt circulate to the ch circuit.
It seems to me as if the water in the NTC zone gets too hot and the boiler switches off on CH, because there is no way of getting the water circulated out of the boiler and therefore it overheats. This problem doesnt occur when running dhw hotwater from the tap and it appears to cool down the heat exchanger. I dont think the NTC sensor is faulty as it only cuts the gas out when its pipe is really hot.
I tried flushing water through the rads to make sure not blocked and okay. Also i reverse flushed water from the return circuit round the rads and backwards up into the boiler and out the pressure overflow to see if flow can go that way and to dislodge any debris and it flushed backwards fine.
I am suspecting the ch valve in the divertor (behind the dhw heat exchanger) is either jammed for DHW and not letting ch water flow. Or there is some reason a sensor or something is signalling to it to remain locked in the DHW position and not CH.
Please can anyone pour light on to this one ?
Also can anyone advise where instructions or for this boiler or associated diagrams.?
Many thanks
Dave
Any advice on this problem Id really appreciate.
Friends Vaillant Sine stopped working. He had 2 plumbers round saying the boiler needed to be replaced for wrong reasons (ignitor not working no parts availalbility) etc.
Ignitor worked fine, but i found the overheat switch open circuit, so i pushed the black knob in and it started to work agaiin for DHW.
When the central heating button gets clicked though the boiler fires up for about 15 seconds, initially full rate, then half rate, then it cuts out.
I checked the signals to the pump and they run when ch is on.
Hot water seems to be being circulated around the inner boiler but not to the central heating circuit.
If I remove the nTc purple wire it fires up fine, but still doesnt circulate to the ch circuit.
It seems to me as if the water in the NTC zone gets too hot and the boiler switches off on CH, because there is no way of getting the water circulated out of the boiler and therefore it overheats. This problem doesnt occur when running dhw hotwater from the tap and it appears to cool down the heat exchanger. I dont think the NTC sensor is faulty as it only cuts the gas out when its pipe is really hot.
I tried flushing water through the rads to make sure not blocked and okay. Also i reverse flushed water from the return circuit round the rads and backwards up into the boiler and out the pressure overflow to see if flow can go that way and to dislodge any debris and it flushed backwards fine.
I am suspecting the ch valve in the divertor (behind the dhw heat exchanger) is either jammed for DHW and not letting ch water flow. Or there is some reason a sensor or something is signalling to it to remain locked in the DHW position and not CH.
Please can anyone pour light on to this one ?
Also can anyone advise where instructions or for this boiler or associated diagrams.?
Many thanks
Dave