hi there - would appreciate advice from anyone who can help
have vaillant turbomax 828 approx 5 yrs old
problem common to heating & hot water - burner seems only to ignite when it feels like it , fan starts- ignition process begins- sometimes ignites, sometimes will not ??
have replaced diverter valve complete- have also removed pcb & tried it another boiler - worked fine
any advice welcome thanks
 
Sponsored Links
Sponsored Links
Its the air pressure switch. Can you see a good spark inside the combustion chamber before it locks out?

Saw a turbomax the other day with a low water pressure switch wired in series with the gas valve so make sure your pressure is atleast 1bar.

Could also jsut need the pressures adjusting (Corgi job!)
 
thanks to all for prompt replies re- poss sticky aps - is there a correct method for testing aps ? as i have removed it , gently blown into it & can feel what i assume is a diaphragm moving in / out . and the best bit....... on refitting all seems ok ! too early to hang the flags out ??
 