HI all
i have a vaillant turbo max VUW 242 E ,date of manufacture is 1998 ,it is being used in a commercial premises and is subject to very high hot water demand.and small heating load of six small rads
it is serviced religiously . i have found that diverter valves are only lasting 9 months at the most , i have fitted a new one today. our problem is maintaining consistent hot water temperature.
The dial on the boiler is set to 8 and the boiler temp gauge shows just over 80 degrees ,system pressure is regularly checked and is 1 bar .
the only way i can get the water temp reasonably high is to partially close the flow restrictor controlling flow of cold mains water into the diverter valve ,currently it is just over 1/4 turn open .any less than this and there is not enough pressure to open the diverter valve fully and make the diverter valve micro switch .any more and the flow rate appears too great for the DHW heat exchanger to cope with and the hot water becomes progressively colder .i have adjusted the position of the switch and it now works.
can any one tell me how to set up the position of the switch correctly and how far open should the flow restrictor be set .
many thanks
i have a vaillant turbo max VUW 242 E ,date of manufacture is 1998 ,it is being used in a commercial premises and is subject to very high hot water demand.and small heating load of six small rads
it is serviced religiously . i have found that diverter valves are only lasting 9 months at the most , i have fitted a new one today. our problem is maintaining consistent hot water temperature.
The dial on the boiler is set to 8 and the boiler temp gauge shows just over 80 degrees ,system pressure is regularly checked and is 1 bar .
the only way i can get the water temp reasonably high is to partially close the flow restrictor controlling flow of cold mains water into the diverter valve ,currently it is just over 1/4 turn open .any less than this and there is not enough pressure to open the diverter valve fully and make the diverter valve micro switch .any more and the flow rate appears too great for the DHW heat exchanger to cope with and the hot water becomes progressively colder .i have adjusted the position of the switch and it now works.
can any one tell me how to set up the position of the switch correctly and how far open should the flow restrictor be set .
many thanks