Hi
Firstly,
My sensor is failed and I am need of a replacement unit. So far I have found its around £180 for this unit on its own! Its an NTC sensor with a radio transmitter and a small solar panel hardly a fortune to produce.
I have seen online that glow worm (owned by Vaillant) use the same unit for their weather compensator and Climapro2 Rf. Its exactly the same, the mounting plate, and button to start the data connection, even the MHz frequency shown is the same 868, and its Ebus connected so I am going to try one, as the glow worm unit is around £45. I can always send it back if it does not work.
Any Vaillant engineers on here seen these on Glowworm units? I'd be interested to confirm my conclusion?
Thanks.
Secondly to aid further searchs.
If this sensor fails to send data to the receiver, the default temperature the boiler then uses is 0C. This was buried in the Operators Manual right at the back.
It appears that even in summer mode at the room stat controller, this is calling for the heating to fire up as it thinks outside is 0C but i think only after the frost protection delay timer has been reached. I have frost protection set to ECO, with a 10 hour delay.
The only way I have found to stop the heating coming on at a low temperature, even when automatic mode is set to "System Off", is to turn the heating control dial fully to the left.
Processpaul, buried in a Vaillant instruction book as usual
Firstly,
My sensor is failed and I am need of a replacement unit. So far I have found its around £180 for this unit on its own! Its an NTC sensor with a radio transmitter and a small solar panel hardly a fortune to produce.
I have seen online that glow worm (owned by Vaillant) use the same unit for their weather compensator and Climapro2 Rf. Its exactly the same, the mounting plate, and button to start the data connection, even the MHz frequency shown is the same 868, and its Ebus connected so I am going to try one, as the glow worm unit is around £45. I can always send it back if it does not work.
Any Vaillant engineers on here seen these on Glowworm units? I'd be interested to confirm my conclusion?
Thanks.
Secondly to aid further searchs.
If this sensor fails to send data to the receiver, the default temperature the boiler then uses is 0C. This was buried in the Operators Manual right at the back.
It appears that even in summer mode at the room stat controller, this is calling for the heating to fire up as it thinks outside is 0C but i think only after the frost protection delay timer has been reached. I have frost protection set to ECO, with a 10 hour delay.
The only way I have found to stop the heating coming on at a low temperature, even when automatic mode is set to "System Off", is to turn the heating control dial fully to the left.
Processpaul, buried in a Vaillant instruction book as usual