vaillent ecomax 828 boiler

Joined
30 May 2008
Messages
2
Reaction score
0
Country
United Kingdom
i have an intermitant fault on this boiler .there is noise as if air is in the boiler also the pressure gauge moves up and down by 0.3 bar it does not sound right . i have dropped the pressue right down to zero and checked the expansion vessel it ok at 0.8 bar . I have also vented the system.................help
 
Sponsored Links
How did you "vent the system" ?

Is the cap on the AAV open?

Tony
 
Thanks for the reply, i put 1.5 bar in and vented all rads then undid the cap on the auto vent
 
Sponsored Links
The auto air vent might be blocked!

Putting a little leak detection fluid over the top with the cap removed would show if any air was coming out!

Tony
 