boiler pressurised to 1 bar and holds it steady. Preheat DHW and pressure drops to 0.5 bar. When CH on pressure increases to a max of 2.9 bar. Bolier is Baxi 105e and recommends pressure between 1 and 1.5 bar. I would appreciate views on this problem.

Thankyou

Charlie
 
Sponsored Links
Your pressure vessel / expansion vessel needs pumping up. Lots of posts, do a search.
 
Sponsored Links
ChrisR said:
Your pressure vessel / expansion vessel needs pumping up. Lots of posts, do a search.

yes, have done so guessed the vessel needed inflating or replacing. Just hoping it might be something simple, like a faulty guage. Thanks for the response though. I'll get me kit.....
 