Hello,
My friend moved into a new build house six months ago. He has a Potterton powermax HE floor standing system, which is sealed.

On an outside wall he has a 28mm turned down pipe with a cover over it, which looks like it could be a vent pipe. Recently this has started to drip water (a drip every second).

He's wondering why this has started dripping, and if it's a sealed system why there is actually a vent pipe.

Any ideas?

Thanks
 
Sponsored Links
This is the prv outlet pipe. Should not be dripping. Check filling loop has not been left slightly open so pressure has increased to over 3 bar. Pressure should be around 1-1.2 bar cold.

If this is not the problem call manufacturers in as these are a specialised boiler. As it is new build, builders customer care should do this for him ;)
 
Thanks for such a quick reply.

I had a look at the pressure, and it's at 2 - 2.5 hot. Not sure about when it's cold as he had his heating on. Would the filling loop be inside the unit? I haven't had the front off to take a look as yet.

He was going to call the building firm, but was just wondering if it was something minor he could sort out himself.

Incidentaly what is a PRV outlet pipe? Is it like an overflow?
 
Sponsored Links
benjamin31 said:
Incidentaly what is a PRV outlet pipe? Is it like an overflow?

Very much like, its a discharge pipe for the pressure release valve, in 28mm because of the length of pipe run. Like the 15mm on a combi, ect.
 