just had a gas safety on a baxi BBU and there was a slight prob with the vent size (needs 90mm2 only got 60ish), this got me thinking
If a BBU has an input of 20kw (boiler) and 5kw(fire front) then you add them together = 25 - 7kw allowance means that the vent is calculated on 19kw.
but if you had a seperate 20kw boiler and 5kw fire in the same room you would take the 20kw boiler only and after 7kw allowance the ventilation calculation will be based on 13kw and not 19kw.
why is this? (or have i read it wrong in the Viper book).
If a BBU has an input of 20kw (boiler) and 5kw(fire front) then you add them together = 25 - 7kw allowance means that the vent is calculated on 19kw.
but if you had a seperate 20kw boiler and 5kw fire in the same room you would take the 20kw boiler only and after 7kw allowance the ventilation calculation will be based on 13kw and not 19kw.
why is this? (or have i read it wrong in the Viper book).