VOKERA LINEA 28 DIVERTOR VALVE

Joined
11 Nov 2005
Messages
3
Reaction score
0
Location
Leeds
Country
United Kingdom
Could anybody give me the pinouts from the M11 port on a 2002 linea 28 boiler please I know pin 2 is N (blue) but I dont know pins 1 and 3? Also is the 240v applied or dropped to operate the divertor valve in either heating or DHW? :confused:
 
Sponsored Links
Voltage is applied to pins 1&2 for heating and pins 2&3 for water.
 