Hi all,
I have a Vokera Linea 28he, approx 3 years old (servicing manual: http://cdn0.vokera.co.uk/wp-content/uploads/2009/04/linea-he-combi-boilers-installation.pdf). I have a problem which has been occurring since I bled a radiator then topped up the system pressure again a month or so ago.
- When the central heating is turned on, the pressure in the system goes really high (seems to settle at around 3.2-3.3 bar from what I can tell).
- Overnight when the system is off, the pressure drops to around 0.2 bar so in the morning we have to top up the pressure and reset the boiler. We're topping up the pressure to about 1 bar.
Symptoms are as described on this page, point 3:
//www.diynot.com/wiki/plumbing:faq:faq31
I had hoped this was an expansion vessel top up, and I just had the boiler serviced - the engineer said the expansion vessel pressure was low, topped it up but the problem remained.
The engineer says he thinks this is probably a blockage within the boiler as the system wasn't flushed properly on installation, which is consistent with what's described in the link above. Apparently the pressure release is opening at 3 bar when the system is hot, so when the system cools the pressure drops really low again because so much water has been released by the PRV. The problem is he's not sure of the most likely place for the blockage to know where to look first. Could anybody offer some advice on where he could start so I don't end up paying for days of his time to take my boiler apart bit by bit?
Many thanks,
Strak
I have a Vokera Linea 28he, approx 3 years old (servicing manual: http://cdn0.vokera.co.uk/wp-content/uploads/2009/04/linea-he-combi-boilers-installation.pdf). I have a problem which has been occurring since I bled a radiator then topped up the system pressure again a month or so ago.
- When the central heating is turned on, the pressure in the system goes really high (seems to settle at around 3.2-3.3 bar from what I can tell).
- Overnight when the system is off, the pressure drops to around 0.2 bar so in the morning we have to top up the pressure and reset the boiler. We're topping up the pressure to about 1 bar.
Symptoms are as described on this page, point 3:
//www.diynot.com/wiki/plumbing:faq:faq31
I had hoped this was an expansion vessel top up, and I just had the boiler serviced - the engineer said the expansion vessel pressure was low, topped it up but the problem remained.
The engineer says he thinks this is probably a blockage within the boiler as the system wasn't flushed properly on installation, which is consistent with what's described in the link above. Apparently the pressure release is opening at 3 bar when the system is hot, so when the system cools the pressure drops really low again because so much water has been released by the PRV. The problem is he's not sure of the most likely place for the blockage to know where to look first. Could anybody offer some advice on where he could start so I don't end up paying for days of his time to take my boiler apart bit by bit?
Many thanks,
Strak