vokera Mynute 28 SE boiler

Joined
14 Oct 2009
Messages
1
Reaction score
0
Country
United Kingdom
We have a vokera Mynute 28 96 SE boiler and when the heating is switched on only the boiler makes a loud rattling sound. The pressure remains at a constant 1.5bar however when the pilot light comes on the pressure gauge starts to flicker and then when the pilot light switches off (after only a few mins) the boiler rattles and the pressure gauge stabilises.

When the water is switched on at the same time as the heating the boiler does not rattle.
boiler
 
Sponsored Links
When the water is switched on at the same time as the heating the boiler does not rattle.
boiler

Based on that I would take the view that the pump is working but there is a blockage in the heating circuit ( or all valves are turned off ).

Did this suddenly start or did it come about slowly?

Do you have one or two motor valves? If two what make?

Tony
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top