Hi, I want another wall socket in my kitchen is it ok to use the electric cooker connector unit and run a 2.5mm cable from it as I have a gas cooker so the connector unit is not being used
 
Sponsored Links
If you use this UNUSED cooker termination point then it would be best to replace this with a fused spur connection unit with a 13amp fuse otherwise the 2.5 cable probably won't be properly protected as the main breaker in the fuse board is likely to be too large.

Often kitchen fitters utilise the disused cooker cable providing a small kitchen radial or ring circuit.
 
Is it acceptable practice to run a ring from an old cooker radial? I thought the ring would have to go back to the CU
 
Sponsored Links
I suppose you could treat the redundant cooker radial as a submain, but (1) it is unusual and (2) it is in a kitchen, so not a DIY job.

Much easier to fuse it down to 20A at the CU and run some sockets off a 2.5mm radial.

Looking back to the OP question, and if the kitchen sockets are on a ring, why not just take a spur off one of the existing sockets? Then you will still have the cooker supply available for when you (or the next occupant) get a wife who likes electric hobs :rolleyes:
 
all the wall sockets have tiles around them, I have a old type fuse box (fuse wire) can I just change the fuse wire from 30 amp to 15amp would that be ok
 
you can buy a 20A MCB that will fit in (I have a feeling that you have an old Wylex Standard CU that's dark brown, or cream). Rewirable fuses are prone to abuse. If you put your email address visible in your profile someone may offer you some MCBs to fit.

Can you post a pic of the CU? Some of them are very old and overdue for replacement.
 
nope, not a Wylex. You probably can't get MCBs to fit.

If you are changing to a lower rated fuse, you ought really to fit a smaller (blue-dot) fuseholder in, but I doubt you will find one.

If that's a tail I can see underneath, it looks worryingly old and might be perished rubber. can you stand back and take a wider pic, pref. showing the meter and service head as well?
 
Chivers7 said:
Things that kitchen fitters do are often unacceptable :LOL: ... but this one takes the biscuit http://groups.msn.com/SparkyHeaven/kitchenfitterfromhell.msnw

Is that the best you've got? :LOL:

Meter and cutout in a corner cupboard:

IMGP0636.jpg
 