I am doing some work in an old house which originally had a solid-fuel CH and DHW installed in the 70s. about 1990, this was replaced by an oil-fired system (a Warmflow boiler). I believe the boiler only was changed out, so the existing plumbing would have remained as-was for the original solid fuel system.
Here's an overview of the system:
I think it's "gravity HW, pumped rads."
large cold water storage tank in loft supplying the cylinder (on the firstfloor) and also cold water to the bathroom.
The cylinder is vented back into this tank.
small F&E tank in loft supplying water to the boiler. (the feed pipe tees off to the cylinder on its way down to the boiler)
The boiler has 4 pipes connected which I have identified as follows:
Main feed AND return from HW cylinder
flow to HW cylinder
flow to radiators
return from rads
There is a 2-channel digital programmer wired up to the system, and is functioning in itself OK.
The rads circuit has a brand new Grundfos 1650 on the return leg next to the boiler. (I have just replaced the old seized Euroma pump)
The room stat for the house controls only this circulating pump. (when it gets cold, the pump starts) This stat will not cause the boiler to fire.
There is a frost stat and separate room stat for a vulnerable extension to the house which is isolated by the only zonevalve in the entire system. When the frost stat operates, the TRV opens, the boiler fires and the pump runs. When this remote roomstat operates, only the pump runs.
The boiler will not fire if the CH is turned on at the programmer - only the pump will run.
The boiler will fire if DHW is turned on at the programmer.
There is a stat on the front of the boiler which governs temperature of the DHW (and, I suppose, eventual rad temperature)
I am a bit confused as to how this all hangs together. Apparently the system has been worked on by a number of different engineers in its history. In particular I am perplexed by this:
Lets say its getting abnormally cold in the house in the middle of a sunday, then you might go to the controller and press advance on the CH side. The stat's set for 20C and its 15C in the house, so that is ON. all that happens, though, is that the pump runs and circulates cool water in the rads.
If you are in the know, then you advance both CH and DHW, and then the boiler fires and you start getting heat out of the rads.
Its as if there is a dual channel controller where a single chanel would do...
Also I am perplexed that there is no explicit feed line for the rads. There must be an interconnection between the 2 heat exchangers at the back of the boiler (?)
I have the warmflow manual but there is F.All in it about the exchangers.
Would appreciate professional clarification on the thermodynamics of this system - 'ow duz it work?
I should add - rads are piped in 15mm, DHW is 22mm and other larger sized.
Here's an overview of the system:
I think it's "gravity HW, pumped rads."
large cold water storage tank in loft supplying the cylinder (on the firstfloor) and also cold water to the bathroom.
The cylinder is vented back into this tank.
small F&E tank in loft supplying water to the boiler. (the feed pipe tees off to the cylinder on its way down to the boiler)
The boiler has 4 pipes connected which I have identified as follows:
Main feed AND return from HW cylinder
flow to HW cylinder
flow to radiators
return from rads
There is a 2-channel digital programmer wired up to the system, and is functioning in itself OK.
The rads circuit has a brand new Grundfos 1650 on the return leg next to the boiler. (I have just replaced the old seized Euroma pump)
The room stat for the house controls only this circulating pump. (when it gets cold, the pump starts) This stat will not cause the boiler to fire.
There is a frost stat and separate room stat for a vulnerable extension to the house which is isolated by the only zonevalve in the entire system. When the frost stat operates, the TRV opens, the boiler fires and the pump runs. When this remote roomstat operates, only the pump runs.
The boiler will not fire if the CH is turned on at the programmer - only the pump will run.
The boiler will fire if DHW is turned on at the programmer.
There is a stat on the front of the boiler which governs temperature of the DHW (and, I suppose, eventual rad temperature)
I am a bit confused as to how this all hangs together. Apparently the system has been worked on by a number of different engineers in its history. In particular I am perplexed by this:
Lets say its getting abnormally cold in the house in the middle of a sunday, then you might go to the controller and press advance on the CH side. The stat's set for 20C and its 15C in the house, so that is ON. all that happens, though, is that the pump runs and circulates cool water in the rads.
If you are in the know, then you advance both CH and DHW, and then the boiler fires and you start getting heat out of the rads.
Its as if there is a dual channel controller where a single chanel would do...
Also I am perplexed that there is no explicit feed line for the rads. There must be an interconnection between the 2 heat exchangers at the back of the boiler (?)
I have the warmflow manual but there is F.All in it about the exchangers.
Would appreciate professional clarification on the thermodynamics of this system - 'ow duz it work?
I should add - rads are piped in 15mm, DHW is 22mm and other larger sized.